Is your scaffold tagged 10kN or is it tagged 10kN/m2?
If it's the latter then a 4m x 4m tower as pictured above would need to be capable of supporting 160kN or 16tonne.
I would guess that the pictured scaffold above is a 10kN scaffold. If its on a housing site you will get pallets of bricks which are around 900 square and weigh 10kN which would equate to 12.4kN/m2 Tubs of muck will come in again at arount 10kN.
Dependant on how the platform is loaded it is not to hard to overload the fitting connection at ledger to standard. If the grid is 1.2x1.2 x 10kN+0.25Kn for boards and imposed the imposed load would be 14.76kN as this load may be applied by mechanical means this load needs to be designed for a 25% impact factor = 18.5kN devide this by the SWL of a fitting would require 3 fittings per location.
I do have to say the bracing looks sh1t